1) Losses. Not just the inverter conversion losses, but the V2L operation will consume (from various research I did on exactly your proposal) around 250W quiescent usage for the vehicle's electronics. That's no big deal when you're powering your kettle or oven. But when your house is ticking along at (say 300-400W) then that reduces your efficiency to around 50%.
2) Unlike a G98/G99 compliant hybrid inverter, the V2L cannot be grid tied, so you will need to switch your house from grid power to EV power via a changeover switch, resulting in brief power cut = reset all those clocks again.
3) When operating the house from V2L you will need to have installed TT earthing arrangement and suitable RCD protection.
4) Max of 7kW should be do-able, but if you bust that limit the vehicle will cut off your power. Remember that inductive loads such as fridge-freezers will draw 5x to 10x their rated power briefly on start up.
Not an old EV, but I assume you've read
@Stageshoot's powering of his house from his MG4
V2L Test. 7kW output...
(oh yes, I see you've contributed on that thread already)
A few things the V2X looks after there. It is an interface between your house battery and EV battery or grid connection. It is not intended to feed back into the grid, it is to island your house from the grid and only use grid assist when the load exceeds the V2L capability.
The next bit is assumption on my part, but after reading a lit about the units, this is what I assume is possible. It is basically how a Victron Multiplus and Quattro work, the Quattro can have both the V2L and a generator or mains wired into it at the same time, and depending on how it is programmed, can switch between each supply and a house battery, as required.
The max draw from the EV is programmable, it can use either the mains or in the case of the Quattro, the house battery, as a load assist, seamlessly integrating the grid sinewave via the inverter drawing from the house battery, using the mains to replace any requirement in the house battery as it changes back to a battery charger once the overload is covered, then dropping the mains when no longer required.
The advantage of the V2X, it can be programmed to sense when the house battery is fully charged via the solar, then rather than selling to the grid if the payment is less than the supply, it will store that back in the EV battery for later use when needed.
All happens without operator intervention, the Victron gear is so fast, unless you have a back up generator that it needs to start up, you won't know it had assisted at all. It has a 100% overload capacity, so a 5 kVA inverter can carry a 10 kVA load while it determines if the mains voltage and frequency is stable, if not, the start up the generator, bring it up to speed to check the same voltage and frequency requirements, switches from mains supply to generator supply, then slowly adds the load to allow it to both warm up and adjust to the load.
An incredibly intelligent UPS (Uninterrupted Power Supply) that will only get better once AI is developed to handle these functions and more, like selecting non essential loads that it can put in standby mode, delay high load start ups until the system is capable of accepting them ..... and who knows what else.
The big battery packs over here can do that already, plus voltage a frequency stabilisation, no need for spinning momentum generation to absorb shock loads, they don't voltage and frequency follow, they voltage a frequency generate is required, so fast it is seamless ....
South Australia has used this ability a number of times already over the last few yrs, keeping the grid stable when the other states linked via DC interconnector, drop out because they had issues with their grid stability .....
I only added that last bit to show it's not a fantasy, it has been a reality for a number of yrs ..... It has been available at house level for yrs as well, and it continues to improve ...