Since we purchased our MGZSEV a year ago we have used the MG supplied granny charger plugged into our carport 3pin 13amp socket for most of its charging.
Recently whilst charging the power to the socket failed & on investigation we found that the other 2 sockets on that ring main were also dead.
Eventually we found a burnt out junction box in the roof of the carport which was a professionally built house extension of some 15 years. As far as we know the wiring had been installed by a qualified electrician. The carport circuit was taken off the existing upstairs ring main of 4x13 amp sockets back to an old fashioned 30amp fuse as originally installed some 45 years since.
In theory the circuit should have been ok as 30amps will give 7kW of power, the granny charger taking 2.2kW plus say a hoover at 1kW plus say a fan heater at 2kW total 5.2kW. However there are several factors that make this assumption erroneous. Firstly the granny charger will take 2.2kW continuously for many hours unlike a hoover for 1/2hr & a fan heater on & off. Therefore any heat build up in the circuit will not readily dissipate until charging ceases. Secondly we estimated that the length of wire from the charger socket back to the fuse box was over 100ft or 30mtrs which would give some voltage drop thereby increasing the current required by the charger. Thirdly we don’t know how well or badly the wires were joined in the junction box & at other places.
I show pictures of the burnt junction box & think we were lucky not to have had a serious house fire. There were scorch marks on the nearby wooden floor joist but I think luckily any flames were subdued by the fibreglass insulation.
Fortunately we have another source of supply on a short run of wire from an RCD box which I shall use even after the problem circuit has been repaired.
Please be warned.