A fridge / freezer is not (usually) a Class II device. Class I appliances require a functional earth and RCD protection which a regular V2L supply does not have.
I am curious as to what an RCD would do for me if i run something off of the V2L.
This is my thinking, please correct me if im wrong.
The V2L in a car is essentially an IT system, meaning it is isolated from ground.
RCD measures if current is lost to ground and trips if it detects less current returning, compared to what is being "sent".
Lets imagine i plug in my freezer that is metal and one of the wires touch the chassis of the freezer.
In a normal Earth Referenced system like the grid, this would mean, if i touch the chassis of the freezer, would be able to send current through the chassis into my hand and then to ground, tripping the RCD.
But with the system in the car being IT, it has no reference to ground so touching one wire should not actually make a completed circuit that you would feel and since no power is lost, the RCD would not trip anyways.
Please tell me where i am wrong here ?
PS. I get that if i were to touch both wires i would be electrocuted, but since the system is not ground tied, it would not trip any inline RCD anyways would it, as the current is not "lost" when it goes through he and nothing is "leaving" the system. ?