V2L function to power the house?

the earth stake does nothing
I disagree.

The earthing rod connects the earth and neutral supply from the vehicle (or generator) to ground on the supply side of the RCD. If a human then touches a faulty device (i.e. one whose external metal casing has become live), some current will flow - via the human - to ground. The RCD will detect the resulting imbalance in current between live and neutral and cut the circuit.
 
I realise I'm late to this party, but it might be worth mentioning that I have that bog-standard cheapo VtL adaptor from eBay. I have run a 3 kw kettle from it many many times, and it boils just as quickly as it does when plugged into the mains. I have also run an 800 watt microwave which nominally draws 1.2 kw, and an induction hob rated at 2 kw. I also run smaller stuff like a pump for an airbed and the charger for my e-bike. I once accidentally ran both the kettle and the airbed pump at the same time.

I've mostly done this while out camping, but a couple of times I have run an extension lead into the house and run the kettle and the microwave from this. (One at a time, obviously.)

I haven't had any issues at all and everything seems fine. I'm currently having thoughts about maybe running the extension lead into the house to run a 2 kw electric heater during the day, on 3.5p/unit night-time electricity, given the price of fuel oil this month!

Obviously this has its limitations and is likely to constitute a trip hazard, but it's a hell of a lot better than nothing in a power cut. I think I could probably run the wifi router, my computer, a table lamp and the TV together, continuously (heating is otherwise catered for), and maybe unplug a couple of things to run the kettle or the microwave or the induction hob. I could also plug in the fridge and freezer overnight, I imagine, and if I only opened them momentarily during the day, stuff would probably stay fresh for the duration.
 
I realise I'm late to this party, but it might be worth mentioning that I have that bog-standard cheapo VtL adaptor from eBay. I have run a 3 kw kettle from it many many times, and it boils just as quickly as it does when plugged into the mains. I have also run an 800 watt microwave which nominally draws 1.2 kw, and an induction hob rated at 2 kw. I also run smaller stuff like a pump for an airbed and the charger for my e-bike. I once accidentally ran both the kettle and the airbed pump at the same time.

I've mostly done this while out camping, but a couple of times I have run an extension lead into the house and run the kettle and the microwave from this. (One at a time, obviously.)

I haven't had any issues at all and everything seems fine. I'm currently having thoughts about maybe running the extension lead into the house to run a 2 kw electric heater during the day, on 3.5p/unit night-time electricity, given the price of fuel oil this month!

Obviously this has its limitations and is likely to constitute a trip hazard, but it's a hell of a lot better than nothing in a power cut. I think I could probably run the wifi router, my computer, a table lamp and the TV together, continuously (heating is otherwise catered for), and maybe unplug a couple of things to run the kettle or the microwave or the induction hob. I could also plug in the fridge and freezer overnight, I imagine, and if I only opened them momentarily during the day, stuff would probably stay fresh for the duration.
Same plan for me. No intention of trying to replace my electricity supplier except during a power cut and then only for minimal power.
 
I disagree.

The earthing rod connects the earth and neutral supply from the vehicle (or generator) to ground on the supply side of the RCD. If a human then touches a faulty device (i.e. one whose external metal casing has become live), some current will flow - via the human - to ground. The RCD will detect the resulting imbalance in current between live and neutral and cut the circuit.
Where does the supply, the MG4, connect to the ground? There is no link back to a substation, a transformer earth stake, only the house earth stake maybe ..... neither line one or line 2 are connected to the earth, so there is no active or neutral, just a floating line 1, line 2 and earthing cable on an appliance that has an outside metal surface the user can come in contact with ...... so with the user getting connected across line 1 and line 2, the supply just sees another appliance, there is no path for the imbalance between line 1 and line 2, if the metal case comes into contact with line 1 or line 2, there is already a path back through the earth cable and the earth stake, how is a second earth stake going to improve this situation?

The solution is an RVD, it looks for more that 30mv on the earth circuit, if it sees that, it trips, whether the faulty appliance causes it or a bared live cable and there is a connection back to something connected to the earth circuit .... the RVD will sense more than 30mv and break the circuit, no current had to run through the person because, without either line one or line 2 being connected to the earth cable, these is no circuit between the two live cables .....

It can be hard to get your head around when you have only ever worked with mains power, but I had to learn it all when I did the electrical and computing diploma at TAFE ..... well, the first 3 yrs squeezed into 1 yr, about then the Electrical Engineer who was teaching us told us what we could be earning after we accumulated 7 yrs worth of study ..... I was already making near double that, so I didn't return ... I never did get my head around calculus ....... so I was never going to be advancing on to quantum computing, nor did I have an interest in how to write formal reports that no one would read unless something went wrong and they were looking for someone to blame ......

T1 Terry
 
In the aftermath of Cyclone Alfred when we had no grid power for eight days. From a 2kW generator we ran an extension lead to a small power board in the kitchen. From that we powered our fridge and freezer and ran lights.

We did not run the genny continuously, but enough to keep things cold and frozen.
It had the same output as the MG V2L.

Since we have bought the ZS, we should be able to do the same if needed.

Meanwhile our solar panels enjoyed a rest. No grid reference, no solar power.
 
Where does the supply, the MG4, connect to the ground? There is no link back to a substation, a transformer earth stake, only the house earth stake maybe
That is NOT what I was saying... I specifically said ...
The earthing rod connects the earth and neutral supply from the vehicle (or generator) to ground on the supply side of the RCD.

You need to create a TT earthing arrangement for the RCD to work.

Maybe better explained using this extract from the excellent Victron "Wiring Unlimited" book. The right-most diagram is what I have been detailing in this thread.

1774964610057.webp
 
That is NOT what I was saying... I specifically said ...


You need to create a TT earthing arrangement for the RCD to work.

Maybe better explained using this extract from the excellent Victron "Wiring Unlimited" book. The right-most diagram is what I have been detailing in this thread.

View attachment 44842
See the centre image, it required an earth/neutral bond, there is no earth neutral bond in a floating system, so an RCD will not function, earth stake or not ....
An RVD in the circuit will trip if voltage is seen on the earth circuit, no need to wet the ground and drive in an earth stake. An RV does not have an earthing stake, an off grid house is unlikely to unless someone has made it into an earth/neutral linked system ....

In many ways, a floating system is safer than an earth/neutral linked system, as long as there is an RVD in the circuit .....