Alb
Moderator
- May 11, 2021
- Solutions
- 6
- Gloucestershire driving an MGS5 LR Trophy
Must admit I'm also confused by the description of "burnt out".
If the EVSE is drawing 30 or 32 amps the circuit breaker should be 40 amps.
Not sure what the norm is, but mine has 40 amp protection giving plenty of headroom for a 7.2kwh charger
I believe that @Corindikev has found the problem. He says the breaker should be rated at 40Amps. I've just looked at my installation and it has a 40Amp RCBO
Not sure of the make 'W' but would suggest a better brand and 40A
Interesting - maybe the specification is different in Australia? The UK specification from MG is a maximum AC charge rate of 7kW, not 7.4kW.The MG4 charges at 32 Amps AC. At 230 volts that is 7.4 kW
No, It is not likely to trip - please refer to the curve-B tripping graph in post #22 above. A 32A MCB will not trip until at least 40A is passed through it and then, only after about 3 hours usage.If your circuit breaker and residual current device is 32 Amps it is at its limit and is likely to trip.
Not sure what your point is here? An RCCB does not 'trip' or protect a circuit from an over-current situation. An RCCB only provides protection for earth leakage faults. Its 40A rating specifies the maximum current that may pass through it and, as such, that rating must always be higher than any MCB/RCBO or DNO head-end fuse that protects the circuit it is on.The manufacturers requirements for installation of my EVSE were to install a 40 Amp RCCB at the supply to the EVSE.
I agree with @Everest.The MG4 charges at 32 Amps AC. At 230 volts that is 7.4 kW. The cars internal inverter/charger has a maximum input rate of 6.6kW DC. The difference is losses due to heat and other factors.
The manufacturers requirements for installation of my EVSE were to install a 40 Amp RCCB at the supply to the EVSE. This allows for spikes and surges. The maximum the EVSE will operate at is 32Amps AC though I am able to limit the input as required from 6 to 32 Amps.
Looking over a few months of data, the most my EVSE drew from the AC supply was 7.2x kW, with the car reporting a DC charge rate of 6.4 kW. Peak power draw recorded (by my Iotawatt at the circuit board) in last 12 months was 7.25 kW.The maximum I've ever seen my EVSE deliver to my MG4 is 7.2kW (per the Wallbox app), with the car drawing 6.5kW at that same time.