Yes, obviously. Not sure why you posted that when I originally said and have repeated that a N-E bond must be made at the generation source...
Regarding...
RVD's seem to be an Australian thing and not generally available or used in the UK.
A floating system is relatively safe for connection of one device, but not when there are multiple devices connected to them, as discussed earlier in this thread.
Maybe there is a difference in how the earth/neutral link is made.
In Australia, the earth/neutral link is at the powerboard, after the supply and before the RCD/RVD, but in an RV for instance, if you added an earth/neutral link after an RCD on the supply, like from a house or caravan park. that second earth/neutral link will trip the RCD on the supply side.
For those relying on an RCD, there is a program in the Victron inverter that looks for an earth neutral connection, if it sees one on the supply, it will leave the earth/neutral linking relay open, if it doesn't sense a link and deems the supply is a floating system, it can be set to close the relay to make that connection, changing it from a floating system to a neutral/active system.
The catch there is, if the remote system has been running on the inverter, a floating system, and the earth/neutral link is made via the relay, as soon as shore power is connected, the shore power RCD sees a fault, the earth/neutral is connected and it sees that as an appliance fault, so it trips, the inverter doesn't see a shore power supply, so continues to run on the batteries. The RV user, now thinks they are receiving shore power that they are paying top $$ for, so everything gets turned on ...... and the battery drops out in the middle of the night .... no lights, nothing ....
Those who attempted to add an RCD after the inverter, so the supply would be cut if a fault was sensed, had a 50/50 chance of connecting the earth to the correct line, in a floating system, both lines are active, the problem occurs when the mains supply is plugged in and line connected to earth after the inverter is the active line on the supply ..... the smoke comes out ....
If the caravan park supply is a reverse polarity, because the lawn care and drain cleaner is also the handyman electrician, wires the replacement burnt out 15 amp socket with the active in the neutral spot and the neutral in the active spot ..... now the RCD upstream fails, so no power anyway.
This is why the RVD was originally designed, it is also an RCD and a reverse polarity detector, the ultimate safety switch.
Sadly, most of the people who make the rules regarding the Australian Standards, can't get their head around something new being introduce after they finished their training .... over here it is known as "professor syndrome", I'm the authority, I didn't study this new idea when I was trained, so it couldn't possibly work .....
T1 Terry