Correct - that is not an area of safety concern that I am aware of.
Absolutely - also for those that only have space for a couple of panels in the garden
The key concern is introducing a generation device on the load (= user) side of the existing protection devices such as MCB's or RCD's (or RCBO's). Traditionally all generation equipment should feed into the supply side.
I think I outlined most of my concern in my post #13...
Is the problem that you could be drawing 32amps into the ring main from the grid then adding an additional 3 from the micro inverter which would then exceed the rating of the cable but the mob wouldn't detect it?
That is my main concern, but specifically compounded by the fact that a radial circuit only needs one loose connection at one of the sockets (and I've seen that on multiple occasions) to become two radial circuits, each carrying up to 40+ Amps before any solar production is added to that, all on a single 2.5mm2 T&E cable.
There are other concerns too, such as efficacy of...
Related to that, is the additional concern as to how quickly the plug-in solar system can disconnect in the event of someone touching the live conductor of the circuit that the system is plugged into. In a standard UK house, if a person touched a live connection (due to, for example, a faulty device, or damaged cable) the RCD would trip out, typically within 40mS. Hence, in order to provide the same degree of safety, the plug in solar system would have to disconnect its supply within that time from detecting absence of the connected mains supply (note, that is only two cycles of 50Hz mains AC). Yet the technical requirements to which the devices need to adhere are yet to be defined - they are expected to be announced early summer.