Yes, approved ones are limited but there's tons of unapproved available via the internet, which is the problem with all consumer goods these days.
What's the rush - I charge at 6.0 amps - takes a long time but it does the job.Question is, am I fairly safe to be running this or beginning to push things uncomfortably? I'm tempted to run it a couple of hours and monitor the temperature displayed (it usually goes to about 30 degrees).
No rush as such, though would like to (safely) get as much juice as possible through the Octopus Go cheaper 4-hour windowWhat's the rush - I charge at 6.0 amps - takes a long time but it dies the job
That's not true - a 13A socket is rated at 13A (provided it's from a reputable manufacturer). Ring main circuits in the UK have a 30A fuse but you should check the loads on the rest of the circuit. Few extension leads are actually rated at 13A (and de-rate if coiled too). A 1.5mm² flexible cable is only rated at 10A and many cables are not suitable for outdoor use (UV affects them). If you have to I'd get a proper site extension 2.5mm² cable with a 'commando' type socket which are rated at 15A. I'd also get an electrician to wire an outdoor commando socket to connect it to.Most sockets are only rated for 10A maximum continuous use in the UK. Even 10A is too much if anything else is running on the same circuit. And that assumes perfect wiring.
Attempting to run beyond this at 13A for extended periods is a huge risk for little benefit.
By far the best option is a dedicated outlet with its own circuit breaker and minimal connections. I appreciate this isn't always an option but it is senseless to take risks.
Often the failure isn't the first time or first ten times you use it, it is a few dozen or hundred times later when the cumulative damage of the thermal stress progressively increases resistance, raises temperatures and results in something burning out. If you are unlucky, it then causes a fire.
False. That's typically peak load, not continuous load for dozens of hours, which is the scenario here. Yes modern new electrical installations (to today's standards) may cope with this but many people don't have those.That's not true - a 13A socket is rated at 13A (provided it's from a reputable manufacturer).
Again false - UK homes have a variety of fuse boxes, fuses, consumer units, circuit breakers and wiring dating back decades. Not all ring mains in the past were installed with 30A fuses. Many homes have old wiring with poor connections that is past its best.Ring main circuits in the UK have a 30A fuse but you should check the loads on the rest of the circuit.
True, you need to be careful with extension leads.Few extension leads are actually rated at 13A (and de-rate if coiled too). A 1.5mm2 flexible cable is only rated at 10A and many cables are not suitable for outdoor use (UV affects them).
This can work well, but then if you can fit a commando and go that expense, not massively more to have a 7kW home charger fitted.If you have to I'd get a proper site extension 2.5mm2 cable with a 'commando' type socket which are rated at 15A. I'd also get an electrician to wire an outdoor commando socket to connect it to.